A contractor is planning for an occupied flush-out to reduce IAQ problems from the construction of an office. The contractor introduces 3,500 cubic feet of outdoor air per square foot of floor area 3 hours prior to the first occupants arriving. What will need to be done next to achieve EQ Credit Construction IAQ Assessment?
A: Continue the flushout until a total of 14,000 cubic feet per square foot of outside air has been delivered to the space
B: Nothing, the flush-out is complete
C: Flush out the space with 3,500 cubic feet of outside air per square foot of floor area each day for a period of 7 days
D: Conduct a baseline IAQ test

参考答案: A

本题解释:
Notes: For an occupied flush-out 3,500 cu. ft. air / sq. ft. must be used prior to occupancy. Ventilation must begin at least 3 hours prior to occupancy until a total of 14,000 cu. ft. air / sq. ft. of air has been introduced.
Option 1 Path 2 still requires a total volume of air of 14,000 cu. ft. / SF to earn the credit, after the initial 3,500 has been introduced.