试卷: LEED AP BD+C模拟题D[查看] A new construction project is going to conduct a phased flush out of the building. The
office building is 75,000 SF. What volume of air is required for flush out before occupancy begins for Indoor Environmental Quality Credit, Construction Indoor Air Quality Management Plan-Before Occupancy? A: 787,500,000 cubic feet B: 225,000,000 cubic feet C: 262,500,000 cubic feet D: 1,050,000,000 cubic feet 参考答案: C
本题解释: Notes:
For a phased occupancy, IEQ Credit 3.2 requires 3,500 cubic feet of air needed per
square foot of building area.
75,000SF X 3,500 = 262,500,000 cubic feet
Note that ‘during construction’ can be confused with ‘pre-occupancy’ because there are no
occupants in the building. However these two terms describe different periods of time in
the LEED rating system. |
|